Hello gurus,
Ignition version: 7.6.6
OS: Ubuntu 12.4 LTS
This morning one of my devices a ControlLogix PLC stopped updating its tags. I first noticed this in the designer as the tags had the red exclamation mark next to them. When viewing tag diagnostics it had a “Config Error”.
I then logged into the server webpage and checked the status of the device under “OPC UA” to which the message for that device was “Disconnected - Browse Pending”.
I then went to the configure tab entered the “Devices” page under “OPC-UA” and tried the “Refresh Browse” This did not fix the issue.
I eventually went to modules under the configure tab and restarted the OPC-UA module. This fixed the problem.
I then checked the time that the tags stopped reading and it coincided with some PLC code edits I did around that time, nothing out of the ordinary.
I then looked at the diagnostics log and found thousands of logs with the same time stamp:
“(I) 6:38:57 AM ControlLogixDriver[SR1] [SR1] Starting browse again because edit number change was detected during last browse.”
And the errors preceding the thousands of errors above:
(I) 6:38:57 AM ControlLogixDriver[SR1] [SR1] Starting browse again because edit number change was detected during last browse.
[WARN] 6:38:57 AM ControlLogixDriver[SR1] [SR1] Browse unsuccessfully.
[WARN] 6:38:57 AM ABControlLogixBrowseRequest [SR1] Browse request failed because fail type is other than TIMEOUT, type = DISCONNECTED.
(I) 6:38:57 AM ABControlLogixBrowseRequest [SR1] Browse request failed because fail type is other than TIMEOUT, type = DISCONNECTED.
[WARN] 6:38:57 AM ABControlLogixTransportPool [SR1] Reseting CIP connection for transaction ID of 17381
[WARN] 6:38:57 AM ABControlLogixTransportPool [SR1] Reseting CIP connection for transaction ID of 17380
[WARN] 6:38:57 AM TimeoutDaemon [ABControlLogixProcessorStatusRequest] request with key “17380” failed due to timeout.
(I) 6:38:49 AM ControlLogixDriver[SR1] [SR1] Processor edit number changed from 41217 to 41729.
(I) 6:38:48 AM ControlLogixDriver[SR1] [SR1] Processor edit number changed from 40193 to 41217.
(I) 6:38:01 AM ControlLogixDriver[SR1] [SR1] Updating tagManager with edit version 40193 with 5845 tags
(I) 6:38:01 AM ABControlLogixBrowseRequest [SR1] Creating browse request using LOW priority.
(I) 6:38:01 AM ControlLogixDriver[SR1] [SR1] Starting browse again because edit number change was detected during last browse.
Any idea why this might happen? I must of made 50-100 PLC edits since ignition went in and this is the first time I’ve seen this.
regards
Mat Kent.